Getting the wiring for my new L25500 and our building is wired for 3 phase.
Coming off the circuit panel I'm showing 214 volts which is less than the 220-240 recommended for the printer. However the directions show (-10% and +6%) for a variance which tells me I'm ok.
But in another section of the directions is says if you only have 208 volts from a 3 phase system, you will need a step up transformer to 240 volts.
So am I safe or do I need a transformer? Any electricians here?
Thanks for your help! Glad to be apart of the signs101 family!