GOOD NEWS:
We just got an awesome new 24x48 ULS laser system!
BAD NEWS:
The toxic fumes are killin' me!
THE STORY SO FAR:
We've got (at present, subject to change) the laser hooked up to an industrial dust-collector blower, venting to the outside via 6" flex hose. This system worked fine (to all appearances) with our Mimaki solvent printer, but on Friday, running our first real jobs on the new (and did I mention AWESOME?) toy, the fumes were so bad I was getting physically ill.
Today, a little investigation showed that the ducting was properly installed (we suspected a loose connection above the drop-ceiling), and a quick going-over with a stick of incense (to find air leaks) showed MASSIVE blow-by at the ventilator. Apparently, dust-collectors are more concerned with particulate (duh) than fumes. I guess we didn't really think this one through too well...
SOOOO.... here's my question for all you smarty-pantses out there:
How do you deal with your laser/solvent printer fumes? What's the best (read: cheapest) solution? I'm thinking restaurant-type ventilator, mounted on the roof or outside wall, but that also sounds kinda pricey. Then again, we just dropped beaucoup bucks on the laser itself, so I reckon it'd be kinda dumb to cheap out on the thing that prevents us all from a ghastly death by poisonous fumes. Also, are there regulatory issues with venting this crap into the atmosphere? Will we need some sort of filtration?
As always, any advice, recommendations, suggestions, snide comments and/or personal, ad hominem attacks are welcomed and appreciated.
ADDENDUM:
Original system flow (pre-laser):
Mimaki --> 6" flex vent pipe up to ceiling, across to back room & down --> dust collector blower --> 6" PVC pipe to outside vent
Current system flow:
Mimaki --> 6" flex vent pipe up to ceiling --\
Laser --> new blower --> 6" flex to ceiling --> Y-connector joining flex pipes, across ceiling to back room & down --> blower --> PVC to outside
So we added the 2nd blower from the laser & tied it into the existing vent from the Mimaki, which YES YES we're already going to change since I pointed out that we were getting an ominous buildup of FLAMMABLE, POSSIBLY EXPLOSIVE solvent fumes in the big expensive box full of open flame and lasers and cool stuff like that. So I'm already on that part at least. I just really need to know some recommendations for getting the damn fumes outta here. KTHXBAI.
We just got an awesome new 24x48 ULS laser system!
BAD NEWS:
The toxic fumes are killin' me!
THE STORY SO FAR:
We've got (at present, subject to change) the laser hooked up to an industrial dust-collector blower, venting to the outside via 6" flex hose. This system worked fine (to all appearances) with our Mimaki solvent printer, but on Friday, running our first real jobs on the new (and did I mention AWESOME?) toy, the fumes were so bad I was getting physically ill.
Today, a little investigation showed that the ducting was properly installed (we suspected a loose connection above the drop-ceiling), and a quick going-over with a stick of incense (to find air leaks) showed MASSIVE blow-by at the ventilator. Apparently, dust-collectors are more concerned with particulate (duh) than fumes. I guess we didn't really think this one through too well...
SOOOO.... here's my question for all you smarty-pantses out there:
How do you deal with your laser/solvent printer fumes? What's the best (read: cheapest) solution? I'm thinking restaurant-type ventilator, mounted on the roof or outside wall, but that also sounds kinda pricey. Then again, we just dropped beaucoup bucks on the laser itself, so I reckon it'd be kinda dumb to cheap out on the thing that prevents us all from a ghastly death by poisonous fumes. Also, are there regulatory issues with venting this crap into the atmosphere? Will we need some sort of filtration?
As always, any advice, recommendations, suggestions, snide comments and/or personal, ad hominem attacks are welcomed and appreciated.
ADDENDUM:
Original system flow (pre-laser):
Mimaki --> 6" flex vent pipe up to ceiling, across to back room & down --> dust collector blower --> 6" PVC pipe to outside vent
Current system flow:
Mimaki --> 6" flex vent pipe up to ceiling --\
Laser --> new blower --> 6" flex to ceiling --> Y-connector joining flex pipes, across ceiling to back room & down --> blower --> PVC to outside
So we added the 2nd blower from the laser & tied it into the existing vent from the Mimaki, which YES YES we're already going to change since I pointed out that we were getting an ominous buildup of FLAMMABLE, POSSIBLY EXPLOSIVE solvent fumes in the big expensive box full of open flame and lasers and cool stuff like that. So I'm already on that part at least. I just really need to know some recommendations for getting the damn fumes outta here. KTHXBAI.